C-More to 5/04
I am fairly new to the C-more line of products and have a question. I am trying to connect an EA7-T8c panel to a AB 5/04. Everything works fine connected with the 3 meter cable (EA-SLC-232-CBL), but I need to located this panel about 30 feet away from the PLC, the 5/04 does not have the RJ45 jack theat the previous models did. Any suggestions
|
|
#2
|
|||
|
|||
|
MAGOO5150, as far as a supplier for D-sub connectors, I suggest trying
http://www.l-com.com You can save yourself soldering (or crimping) D-sub connectors by using the AutomationDirect Ziplink modules and using standard cables with molded-on D-sub connectors. RS232 can go about 50ft. Use good shielded cable. Is this what you're looking for? |
|
#3
|
|||
|
|||
|
If the run ends up being longer than the specified 50 feet, you could always put an FA-ISOCON at the PLC side and use RS-422.
The C-more panel doesn't need the ISOCON because it has RS-422/485 built in (unless you just want total isolation on the network run). |
|
#4
|
|||
|
|||
|
Thanks, for the quick replies. I figured I would have to make up a cable but wasnt sure about the length. Again thanks
|
![]() |