#1
|
|||
|
|||
|
C-More to AB 5/04
I am working on a project where I am monitoring tank levels with ultrasonic sensors w/ 4-20 out. This was done with a 5/04 and a panelview. I replaced the panelview with a C-more 8" and seems to be working okay except I get an error that says PLC-499 ERROR 0X1000. I can not find any info on this. Any suggestions? Any help would be greatly appreciated.
|
|
#2
|
|||
|
|||
|
It means you are calling an address with the C-more that has not been defined in the PLC. Go to the C-more error screen and it will show what address is causing the problem.
|
![]() |