    Hi,
    I configured a GS2-10PS drive with GS-EDRV100 and a DOMORE PLC.

    Can the DST28,$IOMasterError bit to be used to stop the plc program in the event of a loss in communications?


  • #2
    DST28 ($IOMasterErrors) is a 32-bit word containing I/O Master error bits for each I/O Master. Currently there are only two I/O Masters possible, the @LocalIOMaster (which controls the local I/O modules) and the @EthIOMaster (which must be enabled in the CPU Config and controls EBC100 slave bases from the built-in Ethernet port). The LocalIOMaster's error bit it Bit0 of DST28 and the EthIOMaster's error bit it Bit1 of DST28.

    These bits are set ON if that particular I/O Master has slaves that have errors. This error reporting is described in Do-more Help Topic DMD0249.
    Greg Kiser
    Hos Engineering, Inc.
    support@hosteng.com
    http://forum.hosteng.com
    This isn't all true.

    Comment



    • #3
      FYI, if the communication between the GS-EDRV100 and the drive is bad (over the serial connection), then the GS-EDRV100 structure member bit called .IntCommFault will come ON. Currently the Help Topic in Do-more Designer says this bit indicates a bad Ethernet connection, but this is incorrect (and will be corrected in the next release of Do-more Designer); instead, it actually indicates the health of the serial connection between the GS-EDRV100 and the drive itself.
      Greg Kiser
      Hos Engineering, Inc.
      support@hosteng.com
      http://forum.hosteng.com