P-2000 550 to SCADA system with Modbus

Collapse
X
  • Filter
  • Time
  • Show
Clear All
new posts

  • larryhts
    started a topic P-2000 550 to SCADA system with Modbus

    P-2000 550 to SCADA system with Modbus

    I am trying to find out how to set the Modbus node address for the P-2k. I am using Ethernet and will have multiple P-2ks as slaves to the SCADA system. The help files dont reference this.

  • larryhts
    replied
    Jackson, Thanks for the reply. You were right it works very well. Tested it this morning and the data is passing both ways like it should. I guess the IP address is what the Modbus uses. It works well from Mango using the "Modbus IP" drive as the data source. Again thanks for the help.

    Leave a comment:


  • jackson
    replied
    You set the IP address in the CPU setup of the Hardware Configuration. If you are talking about the Unit ID number embedded within the Modbus TCP header: the P2-550 does not require a specific value for this field. It will simply echo back the same value sent in the request (which is the proper behavior for a non-gateway Modbus TCP device).