    Hello, I just updated a broken D4-450 CPU with the new D4-454. After the replacement I'm not able to communicate with devices on Modbus RTU. I'm using port 1 wired as RS422, 9600 baud with no parity. I get no error on the port SP113 and both the RX and TX lights are blinking as long as the modbus device is online. Still I get no values from the modbus device.

    Best regards

    Guğmundur Ben


  • #2
    Unless you wrote ladder logic to configure the port, you have to configure the serial port using DirectSOFT on new hardware. Sadly, the serial port configurations are not part of the project file (unless you have special ladder logic that does that).
    There are 10 kinds of people in this world, those who know binary, and those who do not.

    Comment



    • #3
      Thanks for your response franji1. I had already configured the port in setup secondary com port as it was in the previous (D4-450) CPU. Also it looks funny that the TX/RX lights are blinking while the serial bus is connected but if I pull the power from one of the Modbus devices I get less blinking. I would assume that it was an indication of comunication but I dont get anything as a response to my requests, not even a zero.

      Comment



      • #4
        Not exactly the same CPU but I often saw both lights blinking but no response when the wire pair was swapped.
        thePLCguy

        Bernie