  • P2-550 To an SMC EX260-SEN1 Valve Adapter

    I am having trouble with an EtherNet/IP client to communicate with a SMC EX260-SEN1 ValveBank adapter. I get the TCP connected and the adapter name vendor code but an error 0x128.
    I have tried these on AB processors and this is the first P2-550 for us. Any insight would help. Thanks


  • #2
    Click image for larger version

Name:	eip.JPG
Views:	2
Size:	101.5 KB
ID:	112627 Topic P260 of the help file:

    Click image for larger version  Name:	eip.JPG Views:	1 Size:	101.5 KB ID:	112625
    Last edited by PSeries_Eng; 04-18-2018, 03:08 PM.

    Comment



    • #3
      I have it working now Here are the settings::

      8 bit int, Swap Byte on, and on the output Include Status Header
      input instance = 100
      Integer 8 bit
      Elements 2
      Output Instance = 150 and Include Status Header on
      Integer 8 Bit
      Elements 4
      Config
      Instance = 105
      Integer 8 Bit
      Elements 0
      Thanks Larry