    I have three plc click (slave) and a plc BRX (master) but the ladder logic is not working when i connect the slaves together, the instruction MRX and MWX they give me an error ( operation timed out)


  • #2
    Can you access each slave individually?

    Do all slaves have different addresses?

    Wired correctly?

    Lots of possible failures.

    Comment



    • #3
      if I have access to all the slaves and each port is configured correctly
      I'm using RS232, the addresses are the same in each one, and the connection I think is fine

      Comment



      • #4
        Each individual slave works very well for me but the three of them together are not very slow to respond and there is loss of data

        Comment



        • #5
          Originally posted by ecu95 View Post
          if I have access to all the slaves and each port is configured correctly
          I'm using RS232, the addresses are the same in each one, and the connection I think is fine
          RS232 can't be multi-dropped. You have to use RS485.

          Comment



          • #6
            i did not that

            Comment



            • #7
              Originally posted by ecu95 View Post
              the addresses are the same in each one
              They must have different slave/unit addresses. On serial RS-485, everyone is listening, but only 1 can/should respond. The way they know whether the packet is for them is by the Slave/Unit ID. Hence, all Slave IDs must be unique on the network.