    Is this supposed to work? -- is there something that I have misconfigured?
    I cannot maintain a SLSOFT connection to Solo while P1 is communicating with the Solo


    CPU-485
    Node 10 (master)

    Solo
    Node 1


    9600
    8
    E
    1
    RTU

  • #2
    "I cannot maintain a SLSOFT connection to Solo while P1 is communicating with the Solo"

    as the SOLO uses MODBUS over rs485 I'm pretty sure that is not supposed to work, only one master can be present on rs485.

    Comment


    • #3
      facepalm. Thanks.

      Comment


      • #4
        Yep. Modbus RTU (Serial) can have only 1 Master. Modbus TCP (Ethernet) can have several...