    I have a DL06 and just installed a H0-ECOM100, do I need to edit any ladder logic in the DL06 to enable the H0-ECOM100? I can't seem to get my Cmore HMI to communicate with the DL06. If someone could walk me through the process it would be greatly appreciated.


  • #2
    you set up the ecom100 using netedit

    Comment



    • #3
      I did this, I'll check that the firmware on the DL06 is up to date. Just wanted to be sure I wasn't missing something that had to be done to the DL06 to allow it to recognize the card. On NetEdit I can see that it can access the CPU but it won't communicate with the Cmore HMI.

      Comment



      • #4
        Assuming that Directsoft communicates with the CPU then it must be in the link setup in the Cmore. Ensure that the link to the Ecom is set correctly and that the Cmore and the Ecom are on the same subnet.
        thePLCguy

        Bernie

        Comment