    Hey Guys,

    I feel like I may have bought the wrong PID controller. Trying to run a burnout oven here for jewelry casting which requires a very long ramp/soak sequence that requires me climb at say, 50C/Hr, then stay at Sv when i reach it. Then, climb again at so many degrees per hour. Etc etc. . The problem is, my PID here will go through the ramp soak sequence, but goes full blast from one value to another.

    Thats bad. That causes cracks in molds and possible molten metal everywhere.

    Is there something I'm missing? It works great as just a general temperature regulator.
    If not possible, I'm debating writting my own ramp rate software in something like AdvanceHMI and have it iterate through the ramps via modbus registers. or I may be forced to buy another controller.

    Any thoughts?

    Thanks in advance!





  • #2
    You have to use Ramp/Soak control. See section 12-10 of the quick start guide for the SL4848

    Comment



    • #3
      while the SOLO ramp/soak programing is kind of a pain, I (thought) it should be able to do what you want.

      "Then, climb again at so many degrees per hour."

      "Well, you can't get there from here"

      This forum needs a strikeout attribute, I wrote the following before actually trying it, turns out the SOLO doesn't seem to do "ramp" it will do soak, but it looks like the closest thing to a "ramp" would be a series of short "soaks" at a number of different discrete set points (totally stupid)


      You will have to do some math for that, on the SOLO one sets the set point for a step and the time in the step. For example if you want to ramp from say, 20C to 300C at 50C/Hr. (and assuming you are at 20 when entering the step) you'd set the time at (300-20)/50= 5.6 or 5 hr 36 min. (but that wont actually work)


      One thing to keep in mind if writing your own ramp function to use with the SOLO via Modbus is that as far as I know the SOLO writes to its non-volatile memory (I assume flash) each time a change is made and flash can only tolerate a finite number of writes, perhaps hundreds of thousands, but still, if writing is automated one might hit the limit eventually.
      My guess it that is why the thing won't actually ramp, if it was changing the set point say, every few seconds, that could be hard on the flash

      You might consider just buying a commercial kiln controller.

      Another thought, since you already own the SOLO, and there is no limitation on how often you read from it, on might consider using the SOLO just as a sensor interface and doing the control with something like a CLICK PLC, a C0-01DD1-D is only $100 and has a RS485 to talk to the SOLO, a RS232 for AdvanceHMI or a C-More micro or whatever. While the CLICK does not have a built in PID, it certainly has the math capability to do PID if you write one yourself