    I am doing a wire spooling application using a D-260 cpu, F2-8AD4DA-2 16 bit 8 ch in / 12 bit 4 ch out 0-10 vdc board. The system will consist of a payoff unit using a 10hp ac flux vector drive, a dancer, and a takeup unit suing a 2hp ac flux vector drive. What I am tinkering around with is this: Using the speed pot for an overall master line speed reference signal (0-10 vdc) controlling the takeup speed. What I want to do is use the pid as a trim. For example if the takeup is running at 2000 fpm at 5 vdc reference, naturally the payoff needs to run at the same 2000 fpm. But assuming that 2000 fpm is 5 vdc reference on the payoff as well. The dancer (0-10 vdc) is the input to the pid algorithm (PV). I would like for the 5 volts dc going to the payoff to be made up of approx 90% speed pot ref and 10% pid. Specifically bipolar pid where if the SP is in the middle ie.. 32768=SP (16bit). I can cap the limit of the pid to around 10000 counts or 1.53 volts positive and -10000 counts negative. That way I would have from the 5 volts of reference going to the VFD a maximum of 1.53 of those volts would be from the pid, and the other 3.47 volts would be from the speed pot. What I am running into is by adding the maximum 10000 counts to the maximum value of the speed pot of 65535 (10v) that puts me over the limit. Conversely on the low end of the scale when the negative pid limit of -10000 is added to the speed pot reference I actually go below 0 and the counts roll over. I am currently using a CMPR instruction and watching if the converted Real value goes above or below the thresholds and doing an "ignore" values bit. Is there an easier way to do what I am wanting to do?


  • #2
    You may want to take this with a grain of salt since I don't normally do this kind of control.

    Wouldn't you want the setting from the pot to be the ideal speed of the takeup and the output from the PID to only be a minor correction? In other words, wouldn't the ideal steady state output from the PID be zero?

    I would advise limiting the output (plus or minus) from the PID to a very small value. It should be used as a minor correction only. Then you won't have the math problems.
    thePLCguy

    Bernie

    Comment



    • #3
      Originally posted by bcarlton:
      You may want to take this with a grain of salt since I don't normally do this kind of control.

      Wouldn't you want the setting from the pot to be the ideal speed of the takeup and the output from the PID to only be a minor correction? In other words, wouldn't the ideal steady state output from the PID be zero?

      I would advise limiting the output (plus or minus) from the PID to a very small value. It should be used as a minor correction only. Then you won't have the math problems.
      Hey, I'll take all of the grains of salt I can get. LOL

      Yes I do want the pot to the the ideal setting for the takeup, that is what I am planning. But using a dancer system, I do need a little bit of PID action to keep the system stable. The only time that I am getting the math errors (here on the workbench in trial setup) is at the very bottom ie. Speed pot zero and pid trying to subtract from zero. That is when it rolls around since the pid is in a magnitude plus sign form.

      I am limiting the output to around 1 volt out of the 10 total for the final speed ref.

      Thanks for replying. All help is welcomed.