  • Is There Only One Way To Connect A CLICK PLC To A C-More EA9 HMI?

    Hi all,

    I have already purchased a CLICK model C0-12DRE-D (it has Ethernet, RS-232 and RS-485). Now I'm looking at purchasing a EA9-T7CL-R HMI. Looking at page 13 of the technical installation manual for the HMI it says that with the CLICK only "MODBUS CLICK" is supported:

    https://cdn.automationdirect.com/sta...9userm/ch1.pdf

    Does that means that the only way to interface the PLC to the HMI is via a
    EA-2CBL cable, or can I use the Ethernet connection on the PLC to communicate to the HMI directly via an ethernet cable(this would be ideal for my situation).

    Thanks.


  • #2
    The Click manual says it supports Modbus TCP as a server so try using the generic Modbus TCP client driver on the panel.
    thePLCguy

    Bernie

    Comment



    • #3
      C-more software version 6.4 supports the Click Ethernet driver.