  • I got a problem reading the voltage and frecuency using a Brx plc and siemens Pac3200

    Hi there, I want to know how can I read in real time *(with modbus TCP/IP)* the voltage and frequency using the Siemens Sentron pac3200 and Brx plc
    because I recieve the values in a float format but the plc can not interpret very well the values, Do I need to make a conversion?
    Last edited by Dalfaro21; 08-02-2019, 09:54 AM.


  • #2
    byte/word swap?
    Do other values receive correctly?

    Comment



    • #3
      Look at the SUBSCRIBE instruction. It is used to reformat data for situations like this.