    Since there is not a specific RTD module offer for the P1K, could either the voltage of analog module work? If either could work, which would work best for noise immunity?
    If you've done the very best you can, worrying won't make it any better - Walt Disney


  • #2
    I assume you mean that you would use an RTD transmitter at the RTD? If so, use the MA input module, as RTD to 4-20MA transmitters are quite popular and 4-20MA is much noise immune compared to voltage.

    Comment



    • #3
      Thank you for pointing me in the right direction.

      Edit: My next issue is the RTD is nickel, so its 120 ohm rather than 100 ohm. I'll have to scale the signal, right?

      Edit 2: Never mind, found the Pro-sense XTD-0-UNV transmitter. It can read Nickel RTDs. I need to look better
      Last edited by Ridgeline Mach; 02-01-2018, 12:37 PM.