P2K Not Saving Properly
  • Brandon_
    Why isn't the compiler giving an error on that? More so, why is that an issue at all?
    Interestingly, I ran into the very same problem today. Save program > Program Up to date. Transfer program (runtime) > CPU up to date, but then immediately the program would not be up to day. Re-save the program > program up to date, immediately CPU becomes not up to date.
    Closed everything out, rebooted laptop (it had been up for quite a few days without a reboot), issue disappeared.
    Originally posted by PSeries_Eng View Post
    In your task named "Loading Bay Temperatures" you have a subrung "3.1" that has an END, but is not attached to rung 3. Delete this subrung and it should save.
    Click image for larger version  Name:	Rung.JPG Views:	1 Size:	36.4 KB ID:	111458
    Maybe an update so the software could flag that.
  • PSeries_Eng
  • robertkeenan
    started a topic P2K Not Saving Properly
    I have a PLC which is not saving the project in the normal way.
    Project File Status = Not Saved
    CPU Project Status = Out Of Date
    Transfer the project to the PLC and
    CPU Project Status = Up to Date
    Now save the file to the PC and
    Project File Status = Saved
    I can not get the two of them to be happy with the saved project, either one is out of date or the other is not saved. If I close the project and then reconnect it will say that there is Project Differences, but I know that they are the same. The only error showing on the error history is E04204 DL Buffer > 50% Full and memory usage is 6%. SystemReport.2.17.2018_10.34.15.zip