  • Productivity2000 analog input module P2-08AD-1 Glitch

    When you press the little blue button on the P2-08AD-1 analog input 0-20mA module to enable the status screen, the current value momentarily goes high. This is an issue as any logic that is looking at the current measurement is erroneous triggered. We are using the module to monitor a Fire detector loop circuit. See image below for details.

    Click image for larger version  Name:	Fire Detector loop2.PNG Views:	0 Size:	82.5 KB ID:	122504

    In the logic, a fire system water deluge solenoid is triggered when the current reading is greater than 12mA. What we found is that when the screen times out and you press the blue button, it momentarily energizes the solenoid dumping the fire system. We've had to add a 2sec timer in the logic to delay the solenoid giving the module enough time to stabilize.

    Please investigate and let me know if you can replicate the problem and if a fix is available. Thanks
    -Moses
    Attached Files
    Last edited by machua; 05-04-2019, 10:04 PM.


  • #2
    what hardware revision is you P2-08AD-1? It will be the last one or two digits of the serial number on the module label. Could be either A or A1.
    If you have an urgent issue, please contact AutomationDirect's Technical Support team.

    AutomationDirect.com Technical Support: 1(800) 633-0405 or (770) 844-4200 Email Tech Support

    Comment



    • #3
      Serial number ends with 6A

      Comment



      • #4
        Have you tried swapping the module out with a spare? If needed, call into our RA department to get the P2-08AD-1 replaced.
        If you have an urgent issue, please contact AutomationDirect's Technical Support team.

        AutomationDirect.com Technical Support: 1(800) 633-0405 or (770) 844-4200 Email Tech Support

        Comment



        • #5
          We have 6 modules spread out in 1 local base and 2 remote bases (2 per base). They all randomly do that when awoken, so I think it's something common in them. The 2 second delay seems to have fixed the problem in this application but I just wanted to bring the issue to your attention.

          Comment



          • #6
            Please contact our technical support team to open a trouble ticket. We have contacted our supplier to begin investigating.
            If you have an urgent issue, please contact AutomationDirect's Technical Support team.

            AutomationDirect.com Technical Support: 1(800) 633-0405 or (770) 844-4200 Email Tech Support

            Comment



            • #7
              Sent a PM to you machua. Please review and respond.
              If you have an urgent issue, please contact AutomationDirect's Technical Support team.

              AutomationDirect.com Technical Support: 1(800) 633-0405 or (770) 844-4200 Email Tech Support