    I see that support for Bit Of Word was added for Productivity in 6.31. How do you use it?

    I am familiar with the process for a DL PLC. In my application I would like to display 16 indicators based on the status of each bit. Currently I am unpacking the word into 16 control relays but thought I might be able to avoid that step.

    Thanks


  • #2
    In Productivity Suite all you need to do to access bit of word of an integer tag is is to place a : while typing in a tag name in an instruction. Example: MotorStart:1

    Then in Cmore you would assign the system ID of MotorStart and then the bit you want to access.