    Hello all,

    I have a system with several DL-06's connected to an Cmore EA7 via ethernet. Recently I had to replace a DL-06 with a Click, I have been struggling with getting these two communicating. I am questioning if it is even possible? Can somebody point me in the correct direction.

    Thanks in advance



  • #2
    Use Modbus/TCP for ethernet.
    Clicks address picker can show you the coil/register addresses to use in cmore

    Comment



    • #3
      Thanks for responding. When I try to create a new tag name in the cmore software using the click setup for Modbus/TCP ethernet, it only gives my a choice for memory type 3 or 4 and it will not accept an address. For example I try to enter DF3 using either memory type 3 or 4 and I receive an invalid address error.

      Comment



      • #4
        That is normal. 3 or4 is normal for reading a register from a modbus device.
        Now, go into CLICK->AddressPicker, find the address you need. Select Display Modbus Address. Choose (.) MODBUS 984 Addressing
        (i.e. DF3 =modbus register address 428677)
        Put that modbus register number in CMore's Address field.
        Last edited by kewakl; 10-07-2019, 08:13 AM.

        Comment



        • #5
          I got it, and really appreciate the help.